HELP NEEDED!! (electrical)
« on: December 22, 2007, 19:27:06 »
Hi Guys,
........I need some help with a re-wiring problem, I'll admit straight off that I haven't a clue when it comes to electrics, I recently bought a dual volage generator for not a lot of money as it "only puts out 110 volts" it looks as if it's hardly had any use and the diesel motor starts and runs as sweet as a nut, BUT... as you'll see from the pics the wiring has been "modified" at some time, (God knows why) the 12v dc out seems to work ok and it does show 110v output on the voltmeter, but as you can see nothing goes through the 110v/230v switch, there are 9 wires into the control panel, looking at the circuit diagram the 2off thinner (yellow) wires, (8 & 9) appear to be the 12v circuit and seem to work ok, the earth wire (green/yellow) (3) seems self explanatory, direct to both socket earth pins and then earth stud on panel, it's the rest  (thicker wires) that are as clear as mud to me, No's 4 5 6 & 7 on the diagram and red yellow green and black, which colour = which number, where does it go to on the circuit breaker and then which terminal does it  then go to on the actual voltage switch, I assume  the wires from the alternator go into the centre vertical row of connections on the voltage switch (No's 4 5 & 6) on my pic, but what then goes from No's 1 2 & 3 on the switch to where on the 230v (blue) socket and what goes to where from No's 7 8 & 9 on the switch to the 110v (yellow) socket.   :?  :? (my head hurts now)
......thanks for any help in advance guys, or alternatively (AND EVEN BETTER) is there a competent electrician anywhere in the Peterborough area (25 mile radius) prepared to do the job for me in exchange for a few beer tokens??? (I'll even bring the Genny to you to have it done  :lol:  :lol: )

click on the pics to enlarge them



nil illigitimus carborundum

Offline Hissy

  • Posts: 538
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #1 on: December 22, 2007, 19:48:59 »
Sorry mate.............Totally off subject but. somebody asked me yesterday who had done the picture of my disco. I said it was your misses and that i hadn't seen you on for a while.
Then Hey ! Presto ! here you are  :shock:
Spooky or what ???
Hope your all well >>>>>>>>>>>>

Cheers Andy

As you were  :lol:
REAL MEN DON'T WASTE THEIR HORMONES GROWING HAIR!!

Offline BeJay

  • Posts: 154
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #2 on: December 22, 2007, 20:11:04 »
Hi Andy,
......not been out lately, but hope to get out a bit more in the new year so hopefully see you before too long.....we're all fine this end thanks for asking, hope you and yours are all OK and you all have a great Christmas and New Year.

................cheers, Jack.

nil illigitimus carborundum

Offline joe90

  • Posts: 288
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • Find me on twitter @joeohall
    • Loughborough
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #3 on: December 22, 2007, 20:50:02 »
Do you have a multimeter? i would try belling the circuits out first before connecting anything so you know what connects with what when the switch is moved, i.e when the voltage selection switch is moved to 110v does terminal 4 connect with terminal 7 or terminal 1.

After that you'll be able to identify which are the 240v connectors and likewsie the 110v connectors.

Hope that makes sense.
Joe O'Halloran
2007 Discovery 3 GS 2.7L V6
1979 Series 3 88" 2.25L  Rag Top ERC915T

Offline joe90

  • Posts: 288
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • Find me on twitter @joeohall
    • Loughborough
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #4 on: December 22, 2007, 21:15:35 »
lookign at it again i'd say terminals 1,2 & 3 relate to the 110v side, with terminals 7,8 & 9 relating to the 240v side.

As i see it the center row of termianls on the swith relate as follows
4 = Live on both circuits (110v & 240v)
5 = Neutral return on both circuits (through a breaker when swithched to 240v)
6 = Live when switched to 110v & Neautral when switched to 240v

Hope that makes sense - hook up a multimeter on continutiy test and try the wtich and see what terminals connect with each other

Joe
Joe O'Halloran
2007 Discovery 3 GS 2.7L V6
1979 Series 3 88" 2.25L  Rag Top ERC915T

Offline discowoman

  • Posts: 757
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • my own worst enemy!!
    • Gornal West Midlands
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #5 on: December 22, 2007, 22:08:56 »
Not a clue - sorry
BUT i was chosen to win a brand new Audi when I clickd on pic 3 - and i was 100,000th visitor and had won a MAJOR cash prize on pic 2..lol

Offline SimonHarwood

  • Posts: 76
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #6 on: December 23, 2007, 00:19:27 »
Hmm. It has probably been modified because it does not have 30mA RCD protection on the 110V and 230V outlets.

Did it come with its earth stake and connecting cable? This is essential that this is used every time the generator is used for 110V or 230V.

It won't be difficult to fix, but RCD protection is required to be fitted.
If you would like me to look at it for you, let me know. I am in eastern Leicestershire.

Simon..
Gas Main works are like ants... You never see them in the winter, but once the summer arrives they appear everywhere.

Offline BeJay

  • Posts: 154
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #7 on: December 23, 2007, 01:40:35 »
Hi Guys,
.......thanks for the replies,

Joe90, thanks for the input Joe, did what you suggested and terminal 4 connects to terminal 1 when switched to 230v, 5 to 2, & 6 to 3, so 1 2 & 3 relate to 230v socket and terminal 4 connects to 7 when switched to 110v 5 to 8 & 6 to 9 so 7 8 & 9 relate to 110v socket.

Frontywoman, I refuse to be held liable for the adverts on imageshack, sorry,  :lol:  :lol:

SimonHarwood, cheers Simon, no it didn't come with earth cable and stake, I was planning on using an old piece of cheap/thin jump start cable and an old fishing kit bank stick (as per rod rest/keepnet stick) as a ground if that would be OK, you also have a PM.

.............cheers Jack.

nil illigitimus carborundum

Offline Mutz

  • Posts: 733
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • Norwich, Norfolk.
    • Norwich
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #8 on: December 23, 2007, 19:07:58 »
The fact is :-
A) You need a volt/multi meter
B) Get someone who is qualified to test it/connect it.
C) Unless the cables have the numbers on them somewhere YOU wont have a clue where they come from or what voltage they are.
D) Someone has really butchered the connections.

For yours and other peoples saftey get it 30ma protected with the correct cpc size and proper earth stake and a test certificate on the rcd to make sure it disconnects correctly.

This isnt a toy it can KILL !!!!!!

(No offence intended)
1995 300tdi 90 rebuilt and on the road (but still a project)
1992 Pajero SWB 2.5 Auto (failed its MOT and for sale if you want it)

"I Havn't got a Bad Attitude; you just can't handle my personality"

Offline joe90

  • Posts: 288
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • Find me on twitter @joeohall
    • Loughborough
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #9 on: December 23, 2007, 21:10:50 »
You may find that your local hire centre will fix them someone like HSS who deal. We send alot of our Kit via Travis Perkins for repairs and testing........
Joe O'Halloran
2007 Discovery 3 GS 2.7L V6
1979 Series 3 88" 2.25L  Rag Top ERC915T

Offline BeJay

  • Posts: 154
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #10 on: December 23, 2007, 22:29:52 »
......thanks for any help in advance guys, or alternatively (AND EVEN BETTER) is there a competent electrician anywhere in the Peterborough area (25 mile radius) prepared to do the job for me in exchange for a few beer tokens??? (I'll even bring the Genny to you to have it done   )

Mutz......above is from my original post, it is being rewired by a qualified electrcian and it is being RCD protected, I know my limitations which is why I asked for the help in the first place.......and certainly no offence taken, thanks for your concern.

Joe90......it's sorted, see above, thanks for the input.

.........cheers guys, Jack.

nil illigitimus carborundum

Offline joe90

  • Posts: 288
  • Attack: 100
    Defense: 100
    Attack Member
  • Karma: +0/-0
  • Find me on twitter @joeohall
    • Loughborough
  • Referrals: 0
HELP NEEDED!! (electrical)
« Reply #11 on: December 24, 2007, 12:44:19 »
No worries mate, glad you got it sorted.........just for the record I am a Qualified Spark but for my sins now work as an office dweller!!

Have a Very Merry Crimbo
Joe O'Halloran